Return to index: [Subject] [Thread] [Date] [Author]
Re: 1997 UBC Seismic
[Subject Prev][Subject Next][Thread Prev][Thread Next]- To: seaoc(--nospam--at)seaoc.org
- Subject: Re: 1997 UBC Seismic
- From: "Ron Hamburger" <roh(--nospam--at)eqe.com>
- Date: Tue, 28 Apr 1998 08:14:29 PST
- Priority: normal
On 4/27, Geroge Barclay indicated confusion over the use of the "omega sub 0" factor and the load combinations utilizing this factor in the 1997 code. Response- Equation 30-2, using the "omega sub 0" factor is used only for the design of certain elements, that can fail in a catastrophic manner when subjected to larger forces than required for design of the structure as a whole. Specifically, this includes: 1- chords and collectors 2- members beneath discontinuous elements of the lateral force resisting system. e.g. if a shear wall terminates above the first story, and is supported by columns, the design of those columns would be goverened by Eq. 30-2. 3- the axial strength of steel columns must be designed using Eq. 30-2. 4- Eq. 30-2 must be used when buildings with certain types of irregularities are used. Other than the above cases (and where noted elsewhere in the code0 the Eq. 30-1 governs. Ronald O. Hamburger, SE Regional Manager EQE International, Inc. San Francisco, California
- References:
- 1997 UBC Seismic
- From: George Barclay
- 1997 UBC Seismic
- Prev by Subject: RE: 1997 UBC Seismic
- Next by Subject: Re: 1997 UBC Seismic
- Previous by thread: 1997 UBC Seismic
- Next by thread: RE: 1997 UBC Seismic
- About this archive
- Messages sorted by: [Subject][Thread][Author][Date]